Hi,
I have recently taken over the roles and responsibiliteis of someone who spent the last 20 years managing our campus fiber backbone. As you can imagine, there was some knowledge that walked out the door. We are in the process making decisions on how many strands of fiber, and what kind, to pull to buildings going through renovations. Each of these buildings are getting new data closets with upgraded equipment. As a team, we decided multi mode fiber may not be needed in a couple buildings because of who will be occupying the location. Because of that, we are wonder what might be best practice in determining how many strands of single mode fiber we should pull in. In one building we have 4 strands of single mode going to a location where we are considering not pulling multi mode. So the question is…how many strands of single mode should we have going to that location with scalability and flexibility in mind? My immediate/limited experience with structured cabling has me wondering if anyone has come across this type of scenario, and what they did about it?

Thanks! 

Mike Finnel | Technical Services Supervisor | Marquette University IT Services | 414-288-8010
********** Participation and subscription information for this EDUCAUSE Constituent Group discussion list can be found at http://www.educause.edu/groups/.

Comments

The cost of labor to pull a new cable far outweighs the cost of fiber cable itself, so if you are pulling new cable, always pull much more than you need today, even if you don't terminate all of the strands now. This especially holds true for outside plant cabling. Given that each link typically needs 2 strands, and each piece of equipment may need multiple links for redundancy, 4 strands only gets you one piece of redundantly-linked equipment and no spare strands. Always plan on having at least 2 spare strands at each equipment location so you can swap over to them in case something happens. Common cable strand counts are 6, 12, 24, 36, 48, 72, 144, 288. For small locations with one or two equipment closets I would pull at least a 12 strand cable, if not 24. Perhaps 12 strands per closet, but it depends on your topology (whether you plan to home-run closets to a main distribution point inside the building, or to an aggregation point in another building). Terminating the fiber ends with connectors can be a time consuming (labor intensive) process, so if you are tight on budget you can opt to leave some strands unterminated for future use--just be sure to have good documentation of what you pulled where and what you did and did not terminate. I wouldn't bother with multimode for outside plant, unless you have a legacy application that requires it or you think you can reach everywhere you need to within 300 meters for 10gig/40gig or 100 meters for 100gig multimode OM3/OM4 links. For inside a building or datacenter, using multimode might be worth it depending on the port density since the multimode optics can be 1/3 to 1/4 of the cost of equivalent singlemode optics. But keep in mind that even in this use case, and even with the best OM4 multimode fiber, eventually higher speeds will require an upgrade to singlemode or the use of multi-strand connections to support a single link (like 12-strand MPO for 40GBASE-SR4). If you do need multimode for some legacy reason, check that you get the correct/compatible type. 62.5/125 micron (legacy FDDI cable) won't mate with 50/125 micron (OM2 or the so-called "laser optimized" OM3/OM4) without significant signal loss. Overall, plan for any fiber infrastucture you install to last at least 20 years. On Thu, Jan 02, 2014 at 08:16:48PM +0000, Finnel, Michael wrote: > Hi, > I have recently taken over the roles and responsibiliteis of someone who spent the last 20 years managing our campus fiber backbone. As you can imagine, there was some knowledge that walked out the door. We are in the process making decisions on how many strands of fiber, and what kind, to pull to buildings going through renovations. Each of these buildings are getting new data closets with upgraded equipment. As a team, we decided multi mode fiber may not be needed in a couple buildings because of who will be occupying the location. Because of that, we are wonder what might be best practice in determining how many strands of single mode fiber we should pull in. In one building we have 4 strands of single mode going to a location where we are considering not pulling multi mode. So the question is...how many strands of single mode should we have going to that location with scalability and flexibility in mind? My immediate/limited experience with structured cabling has me wondering if anyone has come across this type of scenario, and what they did about it? > > Thanks! > > Mike Finnel | Technical Services Supervisor | Marquette University IT Services | 414-288-8010 ********** Participation and subscription information for this EDUCAUSE Constituent Group discussion list can be found at http://www.educause.edu/groups/.
Message from iam@st-andrews.ac.uk

I fit 24 SM OS2 nowadays, used to fit 12+12 SM/MM composite cable. The cost of fitting a 24 is only slightly more than a 12 in any case, and you're better to have it, and be looking at it, than looking for it.

Thanks

--
ian

Sent from my phone, please excuse brevity and misspelling.

Minimum of 12 SM for a standard edge closet. We need 8 up front for the stack uplinks.

 

 

Tim Cappalli  |  ACCP /  ACMP /  CCNA
Network Engineer  |  Brandeis University
cappalli@brandeis.edu | (617) 701-7149

 

Message from michael.finnel@marquette.edu

Hi,
I have recently taken over the roles and responsibiliteis of someone who spent the last 20 years managing our campus fiber backbone. As you can imagine, there was some knowledge that walked out the door. We are in the process making decisions on how many strands of fiber, and what kind, to pull to buildings going through renovations. Each of these buildings are getting new data closets with upgraded equipment. As a team, we decided multi mode fiber may not be needed in a couple buildings because of who will be occupying the location. Because of that, we are wonder what might be best practice in determining how many strands of single mode fiber we should pull in. In one building we have 4 strands of single mode going to a location where we are considering not pulling multi mode. So the question is…how many strands of single mode should we have going to that location with scalability and flexibility in mind? My immediate/limited experience with structured cabling has me wondering if anyone has come across this type of scenario, and what they did about it?

Thanks! 

Mike Finnel | Technical Services Supervisor | Marquette University IT Services | 414-288-8010
********** Participation and subscription information for this EDUCAUSE Constituent Group discussion list can be found at http://www.educause.edu/groups/.

The cost of labor to pull a new cable far outweighs the cost of fiber cable itself, so if you are pulling new cable, always pull much more than you need today, even if you don't terminate all of the strands now. This especially holds true for outside plant cabling. Given that each link typically needs 2 strands, and each piece of equipment may need multiple links for redundancy, 4 strands only gets you one piece of redundantly-linked equipment and no spare strands. Always plan on having at least 2 spare strands at each equipment location so you can swap over to them in case something happens. Common cable strand counts are 6, 12, 24, 36, 48, 72, 144, 288. For small locations with one or two equipment closets I would pull at least a 12 strand cable, if not 24. Perhaps 12 strands per closet, but it depends on your topology (whether you plan to home-run closets to a main distribution point inside the building, or to an aggregation point in another building). Terminating the fiber ends with connectors can be a time consuming (labor intensive) process, so if you are tight on budget you can opt to leave some strands unterminated for future use--just be sure to have good documentation of what you pulled where and what you did and did not terminate. I wouldn't bother with multimode for outside plant, unless you have a legacy application that requires it or you think you can reach everywhere you need to within 300 meters for 10gig/40gig or 100 meters for 100gig multimode OM3/OM4 links. For inside a building or datacenter, using multimode might be worth it depending on the port density since the multimode optics can be 1/3 to 1/4 of the cost of equivalent singlemode optics. But keep in mind that even in this use case, and even with the best OM4 multimode fiber, eventually higher speeds will require an upgrade to singlemode or the use of multi-strand connections to support a single link (like 12-strand MPO for 40GBASE-SR4). If you do need multimode for some legacy reason, check that you get the correct/compatible type. 62.5/125 micron (legacy FDDI cable) won't mate with 50/125 micron (OM2 or the so-called "laser optimized" OM3/OM4) without significant signal loss. Overall, plan for any fiber infrastucture you install to last at least 20 years. On Thu, Jan 02, 2014 at 08:16:48PM +0000, Finnel, Michael wrote: > Hi, > I have recently taken over the roles and responsibiliteis of someone who spent the last 20 years managing our campus fiber backbone. As you can imagine, there was some knowledge that walked out the door. We are in the process making decisions on how many strands of fiber, and what kind, to pull to buildings going through renovations. Each of these buildings are getting new data closets with upgraded equipment. As a team, we decided multi mode fiber may not be needed in a couple buildings because of who will be occupying the location. Because of that, we are wonder what might be best practice in determining how many strands of single mode fiber we should pull in. In one building we have 4 strands of single mode going to a location where we are considering not pulling multi mode. So the question is...how many strands of single mode should we have going to that location with scalability and flexibility in mind? My immediate/limited experience with structured cabling has me wondering if anyone has come across this type of scenario, and what they did about it? > > Thanks! > > Mike Finnel | Technical Services Supervisor | Marquette University IT Services | 414-288-8010 ********** Participation and subscription information for this EDUCAUSE Constituent Group discussion list can be found at http://www.educause.edu/groups/.
Message from iam@st-andrews.ac.uk

I fit 24 SM OS2 nowadays, used to fit 12+12 SM/MM composite cable. The cost of fitting a 24 is only slightly more than a 12 in any case, and you're better to have it, and be looking at it, than looking for it.

Thanks

--
ian

Sent from my phone, please excuse brevity and misspelling.

Minimum of 12 SM for a standard edge closet. We need 8 up front for the stack uplinks.

 

 

Tim Cappalli  |  ACCP /  ACMP /  CCNA
Network Engineer  |  Brandeis University
cappalli@brandeis.edu | (617) 701-7149

 

Close
Close


Annual Conference
September 29–October 2
Register Now!

Events for all Levels and Interests

Whether you're looking for a conference to attend face-to-face to connect with peers, or for an online event for team professional development, see what's upcoming.

Close

Digital Badges
Member recognition effort
Earn yours >

Career Center


Leadership and Management Programs

EDUCAUSE Institute
Project Management

 

 

Jump Start Your Career Growth

Explore EDUCAUSE professional development opportunities that match your career aspirations and desired level of time investment through our interactive online guide.

 

Close
EDUCAUSE organizes its efforts around three IT Focus Areas

 

 

Join These Programs If Your Focus Is

Close

Get on the Higher Ed IT Map

Employees of EDUCAUSE member institutions and organizations are invited to create individual profiles.
 

 

Close

2014 Strategic Priorities

  • Building the Profession
  • IT as a Game Changer
  • Foundations


Learn More >

Uncommon Thinking for the Common Good™

EDUCAUSE is the foremost community of higher education IT leaders and professionals.